The Seaward forum will be no longer available from October 2019.

It will be replaced by our new and comprehensive knowledge base on our new website at https://www.seaward.com/gb/support/.

As a result, we are not accepting any new users for the forum.

Earth continuity tests PCs and VDUs

PATGuard 3 Forum

Earth continuity tests PCs and VDUs

Postby edutech » Tue Feb 15, 2011 2:11 pm

We have come across a number of LG monitors and Dell PCs that are failing the earth continuity test in so far as the readings are above the threshold. We are reluctant to fail them as this would cause considerable disruption to the client. We have tested the appliances at several different points with the same result.

The question is: do we fail them or is there some feature with this appliance that would give the high readings?
edutech
 
Posts: 16
Joined: Tue Feb 15, 2011 1:52 pm

Re: Earth continuity tests PCs and VDUs

Postby Grizzly » Tue Feb 15, 2011 10:38 pm

At what sort of reading do they fail at?

Don't forget, the earth continuity pass limit is (0.1 + R) Ω, where R is the resistance of the protective conductor of the supply cord/lead.

So if for example, they were coming in at, say, 0.12Ω, this may still be a pass, as the mains lead might be contributing the 0.02Ω (You would easily know this, as you'll have already performed the seperate test on the detachable mains lead, right?).
However, if you were getting readings of, say, 0.5Ω or even greater, then it's doubtful that the mains lead is contributing that much (again, easily confirmed), so it probably is a fail.

All described in the IEE Code of Practice, section 15.4, pages 73 & 74
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Re: Earth continuity tests PCs and VDUs

Postby Jim Wallace » Wed Feb 16, 2011 8:05 pm

Hi Edutech

If exposed metal parts are connected to protective earth for the purpose of protection against electric shock then there should be a low resistance ( as per the limits in the IEE Code of Practice) path between the exposed metal and protective earth in the mains plug. I have come across IT equipment which has 10's of ohms in the path between exposed metal parts and the protective earth in the mains plug, with no other means of protection (e.g. double insulation). In this case, if the basic insulation failed there would be a real danger of electric shock. Manufactures are not permitted to place components in the protective earth path which increase the resistance above permissible limits.

The metal parts maybe connected to earth for shielding / EMC purposes (rather than for protection against electric shock) but the only person who can give a definitive answer is the manufacturer of the equipment.

One other problem that I have come across in the past is that manufacturers wind the protective earth (inside the appliance) around a ferrite core to comply with EMC regulations. This forms an inductor (coil) which presents an impedance to AC currents. In this case, an AC test current can give a reading higher than the limits in the IEE CoP. This can be confirmed by performing a DC earth test which will give a lower measurement.
User avatar
Jim Wallace
Associate Director, Seaward Product and Technology
 
Posts: 124
Joined: Wed Feb 16, 2011 7:35 pm

Re: Earth continuity tests PCs and VDUs

Postby edutech » Thu Feb 17, 2011 11:39 am

Thank you for the response. The earth continuity tests for the appliances were quite a bit above the threshold and the technician used a short IEC to connect with a pre-calibrated resitance value, so I guess it must be a fail.
edutech
 
Posts: 16
Joined: Tue Feb 15, 2011 1:52 pm


Return to Portable Appliance Testing


Who is online

Users browsing this forum: No registered users and 1 guest

 
 
cron