Some of the preset factory test sequences on the Europa Plus contain the abbreviation NI.
eg 230V HH/PORT NI/1
Can someone clarify what this abbreviation stands for and when should this test sequence be used?
-John
jlms48
 
Posts: 1
Joined: Fri Mar 23, 2012 6:00 pm

Re: Europa Plus -Query on factory-set test sequences

Postby Jim Wallace » Mon Apr 23, 2012 1:56 pm

Hi

The abbreviation stands for 230V Hand Held or Portable Class I sequence with no insulation (NI) test. This sequence would be used on 230V hand held or portable class I equipment that required a protective conductor current (aka earth leakage) measurement but not an insulation resistance test.

The factory set test sequences are shown on page 92 of the operating instructions. The table shows the factory set limits for each sequence. If a test is not included in a sequence the word "skip" will be shown in place of the limit to indicate that the test is "skipped" in that sequence.