The Seaward forum will be no longer available from October 2019.

It will be replaced by our new and comprehensive knowledge base on our new website at https://www.seaward.com/gb/support/.

As a result, we are not accepting any new users for the forum.

Testing a kettle

PATGuard 3 Forum

Testing a kettle

Postby LordAzrael76 » Fri Jul 22, 2011 11:02 pm

I'm just playing with my Supernova XE at present whilst awaiting my C&G course (probably October as it's a free course due to pending MoD unemployment) and have been trying some of my household items, but I can't get either of my kettles to pass the initial earth bond test. The first kettle is a cheapy Tesco plastic jug kettle with easy access to an element (which is new and clean) and the second kettle is an expensive Prestige model with a flat heater plate which I can only hold the earth clip against.

When I run the standard class 1 test on these the test starts with the earth bond test and I always get a reading of >19.99 ohms giving me an instant fail.

Is there something blatantly obvious I'm missing with this or is there a way around it?
(I apologise in advance if it is covered in the COP, but I've only just ordered a copy and it hasn't arrived yet.)

thanks
LordAzrael76
 
Posts: 10
Joined: Wed Jul 20, 2011 8:41 pm

Re: Testing a kettle

Postby Grizzly » Sun Jul 24, 2011 12:35 am

You have plugged the kettle's 13A plug into the Supernova, haven't you?
Obvious, I know, but I've seen people start test sequences without having done so.
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Re: Testing a kettle

Postby LordAzrael76 » Sun Jul 24, 2011 6:30 pm

Yes, definately remembered that :)
LordAzrael76
 
Posts: 10
Joined: Wed Jul 20, 2011 8:41 pm

Re: Testing a kettle

Postby benson » Mon Jul 25, 2011 1:12 pm

The PAT I use doesn't support the earth bond test. The tester may perform an earth continuity test automatically before it performs the earth bond test. Some PAT's claim to perform earth bond tests although in r reality they are only capable of performing. earth continuity or screen tests.
benson
 
Posts: 3
Joined: Tue Jul 19, 2011 9:32 am

Re: Testing a kettle

Postby Grizzly » Mon Jul 25, 2011 2:29 pm

Hi benson,

Interesting.
Which particular PAT units are you refering to, and what do you consider to be the difference between an earth bond test and an earth continuity test?
Are you refering to the test current used (25A as opposed to 100mA, for example) or something else?
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Re: Testing a kettle

Postby Grizzly » Mon Jul 25, 2011 2:35 pm

To LordAzrael76,

Another thought: have you inadvertantly selected a lead earth bond test (via the onboard IEC connector) as opposed to an appliance earth bond test (via the test clip lead)?
Just a wild guess, but if that had occured, it could explain the total fail (>19.99 ohm)
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Re: Testing a kettle

Postby LordAzrael76 » Mon Jul 25, 2011 7:24 pm

Hi,
I just selected the test setup that's been programmed into the unit as a class 1 mov/stat item. The settings are:
Earth bond output 25A Limit 0.10 ohm dur 5s
Insulation 500v limit 1Mohm dur 2s
Leakage 230v limit 3.50mA dur 5s

The kettle is plugged into the unit and the earth lead is attached from the unit's main earth bond socket to the kettle element.
I've just tried it again and it still gives the same readings.
LordAzrael76
 
Posts: 10
Joined: Wed Jul 20, 2011 8:41 pm

Re: Testing a kettle

Postby Grizzly » Mon Jul 25, 2011 7:55 pm

I take it that the Supernova gives an earth bond pass on other Class I appliances?
If so, it may well be that the kettle does have an earth bond problem. Have you tried checking for earth continuity with something like a multimeter, just to see if an earth is indeed present?
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Re: Testing a kettle

Postby LordAzrael76 » Mon Jul 25, 2011 11:07 pm

Hi,I was just trying a few other tests and have discovered the issue. On getting the same results on my iron, I wiggled the earth lead a bit during the test and it changed dramatically. So I removed the connector on the end of the earth lead to find the wires disconnected! The problem with buying second hand I suppose. Never mind, I've found the problem, but does anyone know which wire connects to each terminal in the plug (pat tester end, labelled 1, 2 & 3)? Many thanks
Derek
LordAzrael76
 
Posts: 10
Joined: Wed Jul 20, 2011 8:41 pm

Re: Testing a kettle

Postby Grizzly » Tue Jul 26, 2011 1:57 pm

LordAzrael76 wrote:... does anyone know which wire connects to each terminal in the plug (pat tester end, labelled 1, 2 & 3)?


Glad you've got to the bottom of it!

It doesn't actually matter which wires in the 3-core flex connects to which pins of the 3-pin XLR connector. The Supernova uses the 4-wire method to ignore the resistance of the test lead, and so all 3 cores are connected to the same place on the croc-clip end of the test lead.
For info, my Supernova test lead is wired thus:

Pin 1 Blue
Pin 2 Brown
Pin 3 Green/yellow

but as I said, it doesn't actually matter.

More info on the 4-wire method here: http://www.allaboutcircuits.com/vol_1/chpt_8/9.html
C&G 2377 -01 & -02
User avatar
Grizzly
 
Posts: 116
Joined: Tue Feb 08, 2011 3:27 pm

Next

Return to Portable Appliance Testing


Who is online

Users browsing this forum: No registered users and 3 guests