PostPosted: Fri Jan 17, 2014 4:15 pm
by cooie
Is it possible to PA test computers and other IT equipment with the Prime Test 100? I can't see a way to do it without a 500v insulation test.
Anyone using this model on IT equipment?

Re: PATesting IT equipment with Prime Test 100

PostPosted: Fri Jan 17, 2014 4:45 pm
by Grizzly
IT kit shouldn't have any problem with a 500V IR test.
It's the reduced current earth bond test that's the important one.

The 250V IR test was introduced to enable proper testing of surge protected leads, etc.

Re: PATesting IT equipment with Prime Test 100

PostPosted: Mon Jan 27, 2014 4:18 pm
by Christopher Coates
Dear Cooie,

The 500 V DC test is suitable for IT equipment that is CE marked. CE marked IT equipment should comply with the requirements of BS EN60950, which states that the equipment can withstand a dielectric strength test of 1500V r.m.s.

Christopher Coates
Technical Sales Engineer
Seaward