The Seaward forum will be no longer available from October 2019.

It will be replaced by our new and comprehensive knowledge base on our new website at https://www.seaward.com/gb/support/.

As a result, we are not accepting any new users for the forum.

Europa Plus -Query on factory-set test sequences

PATGuard 3 Forum

Europa Plus -Query on factory-set test sequences

Postby jlms48 » Sat Apr 21, 2012 5:22 pm

Hi,
Some of the preset factory test sequences on the Europa Plus contain the abbreviation NI.
eg 230V HH/PORT NI/1
Can someone clarify what this abbreviation stands for and when should this test sequence be used?
-John
jlms48
 
Posts: 1
Joined: Fri Mar 23, 2012 6:00 pm

Re: Europa Plus -Query on factory-set test sequences

Postby Jim Wallace » Mon Apr 23, 2012 1:56 pm

Hi

The abbreviation stands for 230V Hand Held or Portable Class I sequence with no insulation (NI) test. This sequence would be used on 230V hand held or portable class I equipment that required a protective conductor current (aka earth leakage) measurement but not an insulation resistance test.

The factory set test sequences are shown on page 92 of the operating instructions. The table shows the factory set limits for each sequence. If a test is not included in a sequence the word "skip" will be shown in place of the limit to indicate that the test is "skipped" in that sequence.
User avatar
Jim Wallace
Associate Director, Seaward Product and Technology
 
Posts: 124
Joined: Wed Feb 16, 2011 7:35 pm


Return to Portable Appliance Testing


Who is online

Users browsing this forum: No registered users and 3 guests

 
 
cron