The only problem im having at the moment is the Earth Continuity testing for IEC Leads. I have a couple of my own i have been using to practise with the tester but both leads, one brand new are constantly failing the earth continuity test i keep getting a reading of >19.99 ohms which obviously is a fail, i have made the necessary adjustment witht the limit calculator but the lead is only 2m in length. The short IEC lead that came with the tester for testing ext, leads passes the IEC testing with ease.

I cant seem to work out whats causing this failure, if anyone can advise id be very grateful.

Thank you

Re: IEC Lead Testing

PostPosted: Sat Mar 05, 2011 9:12 pm
by Grizzly
Seems obvious, but have you confirmed that earth continuity exists in the leads, using a multimeter or continuity bleeper?
It's a bit strange that the short IEC lead tests OK, but your other leads fail as if no earth were present at all, rather than just slightly over the pass limit.

Re: IEC Lead Testing

PostPosted: Fri Apr 15, 2011 12:45 am
by calibr8
If you get your tester calibrated, they should check this for you (but ask first as some calibration companies don't).

Assuming your IEC leads are OK, it sounds like an intermittent fault with the PAT tester.

The most common cause would be a loose connection in the back of the socket, inside the case, so give the tester a gentle shake and see if the test result changes.

You could also try doing a manual earth continuity test, using the earth bond lead connected to the earth at the 'free' end of the IEC lead (with the 13A plug end connected to the PAT tester)...A low reading would mean that your IEC lead and the connection into the 13A socket are OK.

Re: IEC Lead Testing

PostPosted: Wed May 04, 2011 2:31 pm
by Duff1
Yer sounds an odd one: >19.99ohms means it is off the top of the scale ie the earth is open circuit?
Check the leads carefully. I did come across one case where the earth pin on molded on 13A plugs was insulated the same as for the two live pins!?